Not missing anything. I'm aware it is 3Ø. What I'm saying is all three line currents add up arithmetically to 25.8A. That's saying all three line currents add up on the neutral and there is 0 cancellation. Is that possible? Yes, it is. But the circuit would have to be set up intentionally to do this. So the question is, how much cancellation will occur. This is taking the opposite approach to how much harmonic current will add in the neutral. If 23% cancellation occurs, the neutral conductor current will be at its limit of ampacity (20A is very conservative for 12AWG 90°C-rated wire)... but functionally acceptable.With respect, what you seem to have missed is that isn't a single component. It's 3-p+n. All three phases have non-linear load. It's their combined triple harmonics that flow in the neutral.
Oh, and the CBRD was a 3MW lighting project.
If the CBRD neutral bars overheated, someone messed up. :happyyes: