If neutral overloading is a concern, 4 pole breaker may be used to trip on overload in neutral.
Sahib Senior Member Location India Sep 28, 2017 #81 If neutral overloading is a concern, 4 pole breaker may be used to trip on overload in neutral.
G GoldDigger Moderator Staff member Location Placerville, CA, USA Occupation Retired PV System Designer Sep 28, 2017 #82 Sahib said: If neutral overloading is a concern, 4 pole breaker may be used to trip on overload in neutral. Click to expand... :thumbsup: Unfortunately that is not likely to be found for a standard panelboard.
Sahib said: If neutral overloading is a concern, 4 pole breaker may be used to trip on overload in neutral. Click to expand... :thumbsup: Unfortunately that is not likely to be found for a standard panelboard.