It seems like you are in the testing business I have never even seen a groundrod test can you (or anyone) tell us if on average (in your area) 1 groundrod is around 25 Ohms?

I have tested in the Washington Metro area from less than one ohm to over 100 ohms, for a single 8' electrode. Just west of here over 250 ohms, with 10 rods, a ufer and 150' of #2 bare tinned in the ground.
 
Hi John.Nice to see you here. I am glad you agree.

Please let me know if if that code review happens.

I did Crownshield Ave this AM

I always take their class. Bill's view on this might surprise some. It did me.

I also agree, the 2nd electrode is required in Romeo's example.

I'll call you Romeo when it's set up. Mike's in charge of MECA in this area and e plans on putting one together in Milford probably in February. That's what he's done the last 2 or 3 cycles.

I've taken my past 2 reviews with Bill and Charlie and I've been very impressed with them.

Scott, it's about 40 minutes from you if you're interested.
 
Re: 2nd Ground Rod

Re: 2nd Ground Rod

It really depends on the size of the service entering the building, however the building cold water line is a sufficiant secondary ground, also keep in mind that if there is a steel structure it also require additional grounding.
 
It really depends on the size of the service entering the building, however the building cold water line is a sufficiant secondary ground, also keep in mind that if there is a steel structure it also require additional grounding.

Could you explain what you mean by the service size and secondary ground?

Welcome to the forum. :)
 