..... while I don't agree with the wording, I stand corrected, and I am wrong on my assertion of all travelers being counted as CCC. The submission to the NEC-CMP is below.
(310.15(B)(2)(a),
Exception No. 6 (New))
Submitter: George Stolz, II, Pierce, CO
Recommendation: Add an Exception to read:
Exception No. 6: Of those conductors that are switched cable or raceway
installations, only the maximum number of conductors capable of being
simultaneously energized need to be derated.
Substantiation: In most threeway and fourway switching methods, the load is
alternated between travelers, eliminating the need to include both travelers in
derating.
Panel Meeting Action: Reject
Panel Statement: The proposed exception is not necessary. The present
language of 310.15(B)(2) already permits what the submitter is proposing.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11