How many outlets can be on one 20 amp circuit for an office ? I was always taught 13. Bec 13 x 180 va each receptacle = less than 2400 va. Thanks.
Mike Holt says 13.How many outlets can be on one 20 amp circuit for an office ? I was always taught 13. Bec 13 x 180 va each receptacle = less than 2400 va. Thanks.
Mike Holt says 13.
Is that for load calcs or actual wiring?Mike Holt says 13.
He thinks it's for wiring.Is that for load calcs or actual wiring?
Receptacle Outlets. Except as covered in 220.14(J) and (K), receptacle outlets shall be calculated at not less than
180 volt-amperes for each single or for each multiple receptacle....
What does "single or multiple receptacle" mean? As in 1 on one yoke vs 2-3-4-5 tied together on one yoke? Is there such a thing as a NEMA 2+ yoke? Should the word "multiple" just be "dual"?. said:Receptacle Outlets. Except as covered in 220.14(J) and (K), receptacle outlets shall be calculated at not less than
180 volt-amperes for each single or for each multiple receptacle....
Now a power strip is another thing altogether. What is plugged into receptacle outlets does not count toward the number of receptacle yokes/straps allowed on a circuit.
I was just noting the strip is basically one yoke. What if the outlet was just a jbox for a hard wired strip? The strip then becomes what, "equipment"?Now a power strip is another thing altogether. What is plugged into receptacle outlets does not count toward the number of receptacle yokes/straps allowed on a circuit.
I was just noting the strip is basically one yoke. What if the outlet was just a jbox for a hard wired strip? The strip then becomes what, "equipment"?
(H) Fixed Multioutlet Assemblies. Fixed multioutlet assemblies
used in other than dwelling units or the guest rooms or
guest suites of hotels or motels shall be calculated in accordance
with (H)(1) or (H)(2). For the purposes of this section,
the calculation shall be permitted to be based on the portion
that contains receptacle outlets.
(1) Where appliances are unlikely to be used simultaneously,
each 1.5 m (5 ft) or fraction thereof of each separate and
continuous length shall be considered as one outlet of
not less than 180 volt-amperes.
(2) Where appliances are likely to be used simultaneously,
each 300 mm (1 ft) or fraction thereof shall be considered
as an outlet of not less than 180 volt-amperes.
Those rules are based on length of the yoke? What if two strips are daisy chained with the cord or hardwired interconnect being 8ft?Here is the nec rule for multioutlet assembles