FionaZuppa
Senior Member
- Location
- AZ
- Occupation
- Part Time Electrician (semi retired, old) - EE retired.
One of these (pic), with one BC in the box? One outlet. Two BC's in that box, one for the duplex and one for the switch, it's then two outlets in that box.so what about a two gang box, with a receptacle in one gang and, i dont know, something else that is not a receptacle in the other gang, maybe a switch with a pilot light. Is that entire box an receptacle outlet or just the one gang?
I'll argue that the NEC verbiage supports taps to, because a switched leg is basically a tap with a inline disco. Anything aft of the switch is pulling power off the BC that is inside that box. Just a single switch box, is still an outlet.
A twist? Lets say the switched leg wiring gets terminated/capped 15ft away in a blank covered jbox. Well, the switch yoke to BC is still an outlet because there exists the opportunity to pull power, just need to attach a load, just as a plug (load) is needed on a recept to be able to pull power off the BC wiring.
Almost anything with a yoke that attaches to the BC wiring will be an outlet point.