A duplex receptacle is one outlet...one "receptacle outlet."
Nope. You might want to get out a codebook and read the definition of receptacle.
A duplex receptacle is one outlet...one "receptacle outlet."
Yup.Nope.
I'll take that bet.I bet ya it is.
Yup.
Art 100: Receptacle Outlet: AN OUTLET where one or more receptacles are installed.
A duplex receptacle two receptacles installed on a single outlet.
Keep going....OK, I'll save you guys the trouble.
Outlet. A point on the wiring system at which current is taken
to supply utilization equipment. (CMP-1)
Receptacle. A contact device installed at the outlet for the
connection of an attachment plug, or for the direct connection
of electrical utilization equipment designed to mate with the
corresponding contact device. A single receptacle is a single
contact device with no other contact device on the same yoke.
A multiple receptacle is two or more contact devices on the
same yoke. (CMP-18)
You're response was incompleteI've already responded.
Regarding unteachable...take a look in the mirror.None are so blind as those who refuse to see.
You're unteachable.
I'm done here. You guys continue to duke it out. I'm sure you'll both realize your mistakes some day.
So, in the 1st definition, that's like hard wiring the microwave or drill press in the box where the power is at, in that box is the point at which current is taken.OK, I'll save you guys the trouble.
Outlet. A point on the wiring system at which current is taken
to supply utilization equipment. (CMP-1)
Receptacle. A contact device installed at the outlet for the
connection of an attachment plug, or for the direct connection
of electrical utilization equipment designed to mate with the
corresponding contact device. A single receptacle is a single
contact device with no other contact device on the same yoke.
A multiple receptacle is two or more contact devices on the
same yoke. (CMP-18)
Perhaps if I split a hair on this discussion, we can find a common interpretation. A duplex receptacle installed in a standard 2x4 box is, at the same time both, (1) Two "outlets," and (1) One "receptacle outlet."A duplex receptacle is one outlet, per definition.
I don't think that was the inference in the MH pic. It only shows max VA via ocpd x voltage, then divided that out by 180VA using duplex recepts for that example. It could have been triplex yoke, thus you would still have 13 yokes x 3recept/yoke = 39 receptacles across 7 (SEVEN) outlets, each yoke still only 180VA. So to infer the VA has anything to do with # of recepts on the yoke seems to be false, false by NEC verbiage, and false by the MH example given.I debated whether to get back into this subject. But my 2 hour meeting was cancelled, and I have some time to kill. I do not agree with a limit of 13. I think Larry's post 21 might be saying the same thing. But 220 is about calculations and 210 is about circuits.
Here is some supporting evidence: 220.11 explicitly says that branch circuits that supply lighting or appliances must be provided to supply the calculated load IAW 220.10. This is the only place I can find that ties 220 and 210 together. It does not mention circuits that supply receptacles. I infer that a branch circuit that supplies receptacles need not be based on the calculated load of 180 VA per duplex.
Most of the buildings I design have far fewer than 13 receptacles per circuit. That is a design choice. Bottom line: if you wish to tell me that there is an absolute limit of 13, I will require you to not include article 220 in your reasoning.,
Whaaaaa, no.Perhaps if I split a hair on this discussion, we can find a common interpretation. A duplex receptacle installed in a standard 2x4 box is, at the same time both, (1) Two "outlets," and (1) One "receptacle outlet."
Sadly, the definition of "receptacle outlet" including the notion of things installed at an outlet leaves open the interpretation that the "outlet" is the 2x4 box. That tends to contradict the definition of "outlet," which speaks of where current is taken. You don't take current from the box. You take current from something inside the box, and (arguably) the box is not on the "premises wiring system." So perhaps a revision to the code is in order.
David, would you agree with this?
Receptacle. A contact device installed at the outlet for the connection of an attachment plug, or for the direct connection
of electrical utilization equipment designed to mate with the corresponding contact device. A single receptacle is a single
contact device with no other contact device on the same yoke. A multiple receptacle is two or more contact devices on the
same yoke.
What viewpoint is that?The Article 100 definition of a Receptacle seems to support David's viewpoint.
Nope, it's not.Read the definition of Receptacle Outlet. A duplex receptacle is one outlet, per definition.
What viewpoint is that?
It says "at the outlet". "The contact device" is one or more receptacles, usually on a yoke, by which you physically grab in your hand, along with wire caps and screwdriver as needed, you take that to some hole in the wall or location someplace on Earth, usually a mounted box (NEC requires it), and you literally wire the yoke to the BC wiring. It is in fact that junction point by which the yoke, which has receptacles on it ("the contact device"), takes power (NEC word "current") at a point on the BC wiring, aka The Outlet.
13 outlets which is supported by the definition of a receptacle.7 Boxes...13 outlets...26 receptacles (13 receptacle outlets to be more specific)
Ah, I see the confusion, it's literally just bad grammar and/or bad chocie of wording.Yup.
Art 100: Receptacle Outlet: AN OUTLET where one or more receptacles are installed.
A duplex receptacle two receptacles installed on a single outlet.
Which is wrong. Read my post behind this one.This is what David said:
13 outlets which is supported by the definition of a receptacle.