I was using the 70,000 customers to try get an estimate of the size of a single transformer to support that load. But I also don't think a single transformer was the cause. That is why I mentioned a cascading event.
I have now done a search for the weight of a 100 MVA transformer. Found this site
https://www.btbplaza.com/index.php/...-inventory/items/view/88-100-mva-220-33-kv-09
It lists a weight of 104,900 kg or at 2.2 #/kg the weight is 230,780 # or 115 tons. Huge to quickly change.
It is possible this is the size of the transformer going to our local substation.
.
.
The local substations:
1) West 50th st has Five 138kv-13.8kv transformers each 65 MVA. This station supplies the Hudson network.
2) Astor has Five 138kv-13.8kv transformers each rated 65MVA. This station supplies Herald Square and possibly one other network (Empire).
Both these stations can run with two out of five transformers out of service or two out of five 138kv supply cables out of service.
Ie, West 50th and Astor are each loaded to 195 MVA.
3) West 65th st has ten 138kv-13.8kv transformers each rated 65MVA. Five of the transformers feed one section of 13.8kv gear the other Five feed another section of 13.8kv gear.
Section 1 feeds the Lincoln Square network while section 2 feeds the Plaza network and Rockefeller center network.
Like other stations 65th is also designed for N-2. The station can work with two of the five 138kv feeds out of service or each 13.8kv section can handle the two of the five transformers out of service.
4) West 42nd st has ten 138kv-13.8kv transformers each rated 65MVA. Five of the ten transformers feed one 13.8kv section of gear while the other five of the ten transformers feed a second section of gear.
Section 1 feeds the Pennsylvania network, while section 2 feeds the Columbus Circle network and the Midtown West network. (Midtown west was a chunk taken from the Pennsylvania network to off load section #1 when section #2 was freed up from herald square network being transferred to Astor)
If you do the math, 3 x 65 x 6 = 1,170 MVA of 1,260 MVA.