Hunter, Sutton, Turtle Bay and Roosevelt each have 12 feeders.
7 69kv feeders from Queens Bridge come into East 63rd st. Each 69kv feeder supplies two transformers or 14 in total. 7 supply 13.8kv switchgear in part 1 of East 63rd st while the other 7 supply 13.8kv switchgear in part two of East 63rd st.
A "part" is shown in post 48.
Each 13.8kv main bus section has at least 4 feeder breakers, two feed one network and two feed another network.
A bus fault or feeder breaker failure results only in the clearing of 4 feeders, or two in each network.
The loss of a 69kv feeder results in two transformers de-energizing- or one in each part of the substation.
This again is not problem as the transformer breaker senses the reverse power and opens.
In fact you could loose two 69kv feeds- 4 transformers (two in each part of the station) and not have outages.
46 MVA x 5 = 230 MVA, or 460 MVA for the whole station.
All in all the design is very redundant and over built.
Reason I am using 63rd as an example is because its not far off from most other substations in Manhattan like such as those involved in the blackout.