I don't understand why, given poco configured ring circuits, how one 'leg' can black out, and not be fed from the other here?
:?
~RJ~
Well, your train of thought is on the right track- thats the same question I'm asking >>
All the breakers on a ring bus are normally closed. When a fault happens on a cable, line, or transformer, only the two breakers directly feeding the failed element trip. Power continues to flow around the now open ring.
Often times to prevent a second fault from breaking the the ring in two or more separate halves (forming undesirable circuit configurations), the outgoing terminal disconnect is equipped with a motor operator which opens and the two tripped breakers re-close closing the ring back up but without the failed equipment (due to the disconnect now being open)
Motor disconnect opening:
https://www.youtube.com/watch?v=7jzTeKVLLCE
The GIS version as would be seen at West 49th st:
https://www.youtube.com/watch?v=q5aCilA_47c
And no that arc is not load, but busbar capacitance which gets very extreme at those voltages.
Even if one breaker fails to open (sticks) for a fault, the scheme is still equipped with breaker failure protection.
That means when the two breakers are called to trip, relaying monitors the current and the breakers' auxiliary contacts. If current is still detected passing through either CTs after 6 cycles of tripping being initiated- it means the breaker has jammed. Relaying then initiates the breaker failure sequence where the next breaker over is then tripped. A DDT signal is also sent to trip any remote breakers supplying the line over as its still feeding though the stuck breaker. This ensure the failed element is truly de-energized and the system is not perpetually feeding a fault.
All this takes place under 30 cycles from the start of the first trip initiation.
A stuck breaker results in two elements out of service- however- this is no problem as only 1 transformer and 1 line is removed at West 49th. This is still within the second contingency design. In fact in theory you could loose two transformers and two 345kv cables in secession and not have any over loaded equipment.
Reason for the stuck breaker scheme is that if the jammed breaker is not dealt with the fault will persist possibly clearing the entire station remotely through Zone 2 / Zone 3 MHO or over current. A cleared station is not only lost load, but also severing a power flow path.