jumper
Senior Member
- Location
- 3 Hr 2 Min from Winged Horses
I reread some of my postings and I see how they could have been misinterpreted!- thx
I like that this forum IS hardcore about terminology--I will be more precise going forward.
In the meantime, I'm mostly curious about :
1) what is an OCPD?
2) How specifically does running an EGC to a subpanel ground bar violate 250.24(A)(1). I read 250.24(A)(1 several times. My training and experience ( lol ) tells me its wrong irregardless of
250.24(A)(1) but the verbiage is so damn dense I was unable to make the intellectual link.
I'm not too concerned about solving the issue but I would like to better understand from an practical POV what the possible issues are from such a whacked build out. If those 4 GEC's aren't bonded to metal framing that is hidden then the whole issue is sorta moot and only worthwhile as intellectual fodderThe solution is to snip those 4 GEC's and drop in two new ground rods according to NEC rules.
I began this dialogue in an attempt to learn what sort of problems could be created by landing service GEC's on a subpanel not part of the services per se. The fix is straightforward: Correct buidling GES and unit GEC's to code. Boom!
I hope this is clear sirMy tele can be given by PM if u have any further curiosity about the install's topology. In gratitude, js
First, I removed your phone number. This is an open forum and your privacy is important.
OCPD is Over Current Protection Device=circuit breaker or fuse.
Not sure how I got you caught up in tieing EGCs to 250.24 together. I was trying to say where GECs could be landed. Prolly my bad.
Correct me if I am wrong. The service comes into the building and there is no main disconnect or breaker, but a trough or box where the conductors split up and go to each occupancy.
Therefore, each occupancy has a main panel and breaker.
Correct so far?
If yes, there should be a three wire feed from service trough to each occupancy.
There is not a GEC, connected to the service neutral, in this trough/box that goes to a GES for the building.
I will continue after you answer and correct me if needed.