Back to the 2 basic issues as I see them.
Back to the 2 basic issues as I see them.
Within the scope of the OP's post that I have copied above are two issues that I have not seen clearly addressed as yet. The first is that the Service Disconnecting Means (SDM); which here consists of 4 separate Service Equipment Enclosures (SEE) does no appear to have a Grounding Electrode Conductor (GEC) installed. To correct this you check the Size of the GEC which is required by the sizing of the Service Entry Conductors. In your case that is #6 AWG Cu or #4 AWG Al. As of 2014 NEC the GEC must be installed in accordance with NEC 250.64(D)(3):
"250.64 Grounding Electrode Conductor Installation.
Grounding electrode conductors at the service, at each building or structure where supplied by a feeder(s) or branch circuit(s), or at a separately derived system shall be installed as specified in 250.64(A) through (F).
(D) Building or Structure with Multiple Disconnecting Means in Separate Enclosures. For a service or feeder with two or more disconnecting means in separate enclosures supplying a building or structure, the grounding electrode connections shall be made in accordance with 250.64(D)(1), (D)(2), or (D)(3).
(3) Common Location. A grounding electrode conductor shall be connected in a wireway or other accessible enclosure on the supply side of the disconnecting means to one or more of the following, as applicable:
(1) Grounded service conductor(s)
(2) Equipment grounding conductor installed with the feeder
(3) Supply-side bonding jumper
The connection shall be made with exothermic welding or a connector listed as grounding and bonding equipment. The grounding electrode conductor shall be sized in accordance with 250.66 based on the service-entrance or feeder conductor(s) at the common location where the connection is made."
The second thing that is not clear is if the feeder supplied panels (Commonly called Sub Panels) that are located in the interior of the unit have carefully separated Grounded Current Carrying Conductors (Usually called neutrals) and EGCs. In both the Square D Homeline panel, that is to remain, and in the new panel, that will replace the existing Federal Pacific Electric panel, the "neutral" conductors and the EGCs must be electrically separated and attached only to the corresponding conductor of the Feeder.
If the OP confirms or corrects those 2 problems then he can walk away with a clear conscience.
There is another land mine here in addition to the possibility that additional loads may have been added so as to possibly overload the Service Entry Conductors. Land mine number 2 is that If all 4 of those Service Equipment Enclosures is not fitted with a single Main Disconnecting Means then the number of throws of the hand required to disconnect the service may now exceed the maximum number allowed for a single service.
Back to the 2 basic issues as I see them.
It's likely that at least ONE Grounding Electrode Conductor from one unit's main panel is bonded to ground bar in another unit'subpanel. All 4 units are tapped from one feed from Pacific Gas and Electric. Building ground electrode is most likely not up to code and I have recommended to client that we simply redo the building ground to code. This would involve removing that ( or those ) #8(s) from my customer's sub panel. The Subpanel ground appears to be done with the RMC or EMT used to run the subpanel feed from View attachment 19283View attachment 19284 is service, as there is no discrete wire from that panel coming in to the main panel.
This all began when the customer showed me inspection report questioning why 4 #8's go into his unit. I traced them back and found they were the 4 service Grounding Electrode Conductors....View attachment 19285
Within the scope of the OP's post that I have copied above are two issues that I have not seen clearly addressed as yet. The first is that the Service Disconnecting Means (SDM); which here consists of 4 separate Service Equipment Enclosures (SEE) does no appear to have a Grounding Electrode Conductor (GEC) installed. To correct this you check the Size of the GEC which is required by the sizing of the Service Entry Conductors. In your case that is #6 AWG Cu or #4 AWG Al. As of 2014 NEC the GEC must be installed in accordance with NEC 250.64(D)(3):
"250.64 Grounding Electrode Conductor Installation.
Grounding electrode conductors at the service, at each building or structure where supplied by a feeder(s) or branch circuit(s), or at a separately derived system shall be installed as specified in 250.64(A) through (F).
(D) Building or Structure with Multiple Disconnecting Means in Separate Enclosures. For a service or feeder with two or more disconnecting means in separate enclosures supplying a building or structure, the grounding electrode connections shall be made in accordance with 250.64(D)(1), (D)(2), or (D)(3).
(3) Common Location. A grounding electrode conductor shall be connected in a wireway or other accessible enclosure on the supply side of the disconnecting means to one or more of the following, as applicable:
(1) Grounded service conductor(s)
(2) Equipment grounding conductor installed with the feeder
(3) Supply-side bonding jumper
The connection shall be made with exothermic welding or a connector listed as grounding and bonding equipment. The grounding electrode conductor shall be sized in accordance with 250.66 based on the service-entrance or feeder conductor(s) at the common location where the connection is made."
The second thing that is not clear is if the feeder supplied panels (Commonly called Sub Panels) that are located in the interior of the unit have carefully separated Grounded Current Carrying Conductors (Usually called neutrals) and EGCs. In both the Square D Homeline panel, that is to remain, and in the new panel, that will replace the existing Federal Pacific Electric panel, the "neutral" conductors and the EGCs must be electrically separated and attached only to the corresponding conductor of the Feeder.
If the OP confirms or corrects those 2 problems then he can walk away with a clear conscience.
There is another land mine here in addition to the possibility that additional loads may have been added so as to possibly overload the Service Entry Conductors. Land mine number 2 is that If all 4 of those Service Equipment Enclosures is not fitted with a single Main Disconnecting Means then the number of throws of the hand required to disconnect the service may now exceed the maximum number allowed for a single service.