my mandate has not been to analyze entire building. its a 4 unit condo complex w out a formal HOA.
your points are great,thx
js
QUOTE=al hildenbrand;1884658]What about the Service Entrance conductors?
The conductors in what appears to be a 2 inch conduit? The ampacity of those conductors is possibly the limiting factor. . . not the size of the four (or five) Service Disconnect Overcurrent Protective Devices, or the current carrying capacity of the subpanel feeder conductors.
When a multiple service disconnecting means (your 4 or 5 disconnects) is supplied by a single set of service entrance conductors, the size of the service entrance conductors must be determined by calculating the existing load via Article 220. Your client added an additional 50 A feeder, yes. . . but that doesn't give us any information about what the connected load is. Did your client actually add load that is new and additional to the original calculation done by the electrician that designed the original four-meter/disconnect?
See, a lot of time has passed from the original FPE installation. How many new loads have been added/changed beyond the original as-built loads? The only way to tell, whether the Service Mast Conductors are up to today's load, is to ask after the present day loads, get the habitable area dimensions and to do the Calc. The amperage of the Service Disconnect Overcurrent Protective Devices and/or the current carrying capacity of the Feeders has nothing to do with the outcome.
Edit To Add: I just saw your response about possible 1-1/2" size Service Mast !! The Calculation is even more important as the conductors get smaller. It sounds like the client's adding of the fifth feeder may be a real problem for the Service Mast conductors.