Odd Multiwire Circuit

Status
Not open for further replies.

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Consider the attached picture.

Assuming the circuit breaker handles are tied together, could you legally use a pair of 12-2 NM cables to go to different points in a kitchen, and then combine them back together to come into, say, an island with a single 12-3 NM cable?
 

Attachments

  • odd multiwire.jpg
    odd multiwire.jpg
    10.8 KB · Views: 0

John120/240

Senior Member
Location
Olathe, Kansas
George, what is the intended application or is this just theoritcal ? At # 4 you would have

240V. Handles are tied together so thats kosher. So as to the ring circuit issues..........IDK
 

jeremysterling

Senior Member
Location
Austin, TX
A GFCI receptacle will work just fine.

By that, I hope you mean the recept will trip and not provide any power.

If you have a GFCI wired line/load at outlet "1" and a load on circuit "A" at outlet "4", a portion of the neutral current will run on the circuit "B" neutral homerun. That portion should be enough to trip the GFCI.
 
Last edited:

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
By that, I hope you mean the recept will trip and not provide any power.

If you have a GFCI wired line/load at outlet "1" and a load on circuit "A" at outlet "4", a portion of the neutral current will run on the circuit "B" neutral homerun. That portion should be enough to trip the GFCI.
Its much simpler than that. Just don't try to use the load side terminals of any GFCI receptacle that has line connections at #1, #2, #3, or #4.
 

jeremysterling

Senior Member
Location
Austin, TX
Its much simpler than that. Just don't try to use the load side terminals of any GFCI receptacle that has line connections at #1, #2, #3, or #4.

Agreed.

However, I was contributing to the line of furthering the complicated nature of the OP circuit. What could be simpler than a SABC? Finding a circuit with parallel #12 neutrals, non-grouped MWBC, ActionDave's problematic EMF(!), and GFCI's crammed into every outlet.

Of course, we could plan ahead and put a 1900 box at outlet #3 to make room for your joints.
 