Re: Oops...EMT offset on service
[ October 24, 2005, 01:39 PM: Message edited by: sfav8r ]
[ October 24, 2005, 01:39 PM: Message edited by: sfav8r ]
Have a magnet handy?Originally posted by sfav8r:
Sooo, who decides is a zinc fitting is rigid or not?
Does it matter? "Generally" made of steel and can also be aluminum.Originally posted by LarryFine:
Have a magnet handy?Originally posted by sfav8r:
Sooo, who decides is a zinc fitting is rigid or not?
From the UL?
GENERAL INFORMATION FOR ELECTRICAL EQUIPMENT DIRECTORY
RIGID FERROUS METAL CONDUIT (DYIX)
This category covers rigid ferrous metal conduit that includes standard 10 ft. lengths of straight conduit, with a coupling, special lengths either shorter or longer, with or without a coupling for specific applications or uses, elbows, and nipples in trade sizes 3/8 to 6 (metric designators 12 to 155) inclusive for installation in accordance with Articles 300 and 344 of the National Electrical Code, NFPA 70 (NEC).
Edited 10/25 to add the comment about why DWWT is the correct section.
I agree 100%!Originally posted by sfav8r:
It seems to me that if the manufacturer has it listed in their catalog as rigid and the inspector can't prove otherwise it ought to be approved.
I'd take the stance that you have hence proven your assertion, which is more than "swaying".The Arlington engineer is going to email me something that he thinks may sway the inspector.
More time than I care to admit, however, this particular installation is a bugger to swap out.Originally posted by tshea:
Not to be a stick in the mud...because I agree, if you are right, then prove me wrong.
How much time did you spend proving you are right? You could have replaced all the offsets with "inspector approved" fittings in the same time.
Say it ain't so! This is the craziest thing I've ever heard in my life. But since you say San Francisco, I'm not surprised at all. :roll:Originally posted by sfav8r:
Well, its like this. The final verdict is that the Arlington 6A5 has an AIC rating of 3000 and San Francisco requires an AIC rating of 10,000 on all conduit and fittings prior to a disconnect.
There is a topic right there. Call it "Stupid statement of the day".Originally posted by luke.stickney:
Remember, it's not about code, it's about what the inspector wants.