Oops...EMT offset on service

Merry Christmas
Status
Not open for further replies.
Re: Oops...EMT offset on service

Well, I looked up the UL file which is E60812. It verifies that the standard used for approval was DWTT. According to UL (very helpful folks there) The DWTT standard does include Rigid Conduit fittings and that die-cast zinc are one of the listed materials that can meet that standard.

The inspector originally said "just go get some of the OZ Gedney offsets, they're for rigid." Today I looked up the OZ gedney, and found them to be approved under the exact same DWTT standard.

I guess I don't have much chouce but to take all of the materials to the chief inspector and hope his ego isn't as involved as the district inspectors.
 
Re: Oops...EMT offset on service

sfav8r,

You still may be looking at the wrong fittings over at OZ Gedney if the OZ Gedney nipple came back as DWTT.
From the UL?
GENERAL INFORMATION FOR ELECTRICAL EQUIPMENT DIRECTORY
RIGID FERROUS METAL CONDUIT (DYIX)
This category covers rigid ferrous metal conduit that includes standard 10 ft. lengths of straight conduit, with a coupling, special lengths either shorter or longer, with or without a coupling for specific applications or uses, elbows, and nipples in trade sizes 3/8 to 6 (metric designators 12 to 155) inclusive for installation in accordance with Articles 300 and 344 of the National Electrical Code, NFPA 70 (NEC).
 
Re: Oops...EMT offset on service

Al, thanks for the info.

The reason I referenced DWTT is because the fitting he wanted me to use was approved under DWTT.

There is definitely some confusion because rigid fittings could be approved under DWTT or DYIX. As it turns out, offset nipples (rigid or otherwise) are not under DYIX. They are only approved for the connection between boxes and are approved under DWWT as a connector.

Unfortunately when I look at the actual UL file numbers, they specify some things more clearly that others. Maybe I just don't know how to interpret what's there.

It seems to me that if the manufacturer has it listed in their catalog as rigid and the inspector can't prove otherwise it ought to be approved.

The Arlington engineer is going to email me something that he thinks may sway the inspector.
Edited 10/25 to add the comment about why DWWT is the correct section.

[ October 25, 2005, 04:59 PM: Message edited by: sfav8r ]
 
Re: Oops...EMT offset on service

Originally posted by sfav8r:
It seems to me that if the manufacturer has it listed in their catalog as rigid and the inspector can't prove otherwise it ought to be approved.
I agree 100%!
The Arlington engineer is going to email me something that he thinks may sway the inspector.
I'd take the stance that you have hence proven your assertion, which is more than "swaying".
 
Re: Oops...EMT offset on service

Not to be a stick in the mud...because I agree, if you are right, then prove me wrong.

How much time did you spend proving you are right? You could have replaced all the offsets with "inspector approved" fittings in the same time.
Don't get me wrong, I'm on your side. If you are right and I believe you are, then your fight is right and will pay off in the long run or next job which ever comes first!
 
Re: Oops...EMT offset on service

Originally posted by tshea:
Not to be a stick in the mud...because I agree, if you are right, then prove me wrong.

How much time did you spend proving you are right? You could have replaced all the offsets with "inspector approved" fittings in the same time.
More time than I care to admit, however, this particular installation is a bugger to swap out.

The other thing is, I didn't intend to spend this much time :) I figured I would just fax over the catalog page and I'd be done.

Now, to go change the nipples, I'd have to notify all the tenants again and interupt the contractors that are doing the condo conversion. It's not that I won't do it, I guess after a few hundred "what the heck I'll just do it to get them off my back" you eventually dig in your heels when things get too ridiculous.

The really amazing part about this particular inspector, is the guy seems so reasonable (I know it's hard to believe after all the posts here). But he's real laid back, very professional and comes across as a very reasonable guy. Why he's making a federal case out of this darn thing is very puzzling.
 
Re: Oops...EMT offset on service

Well, its like this. The final verdict is that the Arlington 6A5 has an AIC rating of 3000 and San Francisco requires an AIC rating of 10,000 on all conduit and fittings prior to a disconnect.

No, the amendments don't actually say that of course, they simply say it must be rigid. So now the powers that be say "EVEN IF the fitting is technically rigid, it doesn't meet code because the AIC rating is only 3000."

See how simple that is. If your already amended code doesn,t get the results you want, just add a few things as you go along.

If I sound sarcastic, please forgive me. I'm just sick and tired of the BS in this city.

So, I'll go spend 3 hours of my time to "correct" a perfectly good installation. Viva bureaucracy.
 
Re: Oops...EMT offset on service

Originally posted by sfav8r:
Well, its like this. The final verdict is that the Arlington 6A5 has an AIC rating of 3000 and San Francisco requires an AIC rating of 10,000 on all conduit and fittings prior to a disconnect.
Say it ain't so! This is the craziest thing I've ever heard in my life. But since you say San Francisco, I'm not surprised at all. :roll:
 
Re: Oops...EMT offset on service

what are doing talking about nipples inn san francisco, you sexist pig? :D
 
Re: Oops...EMT offset on service

I suppose they set up an indpendent commision to investigate the AIC rating of die-cast offset nipples, set up many mock services, testing many samples, published the results for indendent review, convened committees, took random surveys, then finally made it law.
 
Re: Oops...EMT offset on service

Funny that he failed you an this. I just did the same installation for a two unit building on Treat Street in San Francisco and passed with die cast offset nipples. The only thing the inspector called me on was that I had separated my neutrals and grounds in the disconnect. I have always been of the understanding that you combined your neutrals and grounds in the first piece of equipment that your service enter into, which in my case was the three gang meter socket. But the inspector made me combine them all together in the disconnects in order to give me the green tag.

Remember, it's not about code, it's about what the inspector wants. And most of them have little to no experience other then taking a couple of classes and passing a test.
 
Re: Oops...EMT offset on service

Originally posted by luke.stickney:

Remember, it's not about code, it's about what the inspector wants.
There is a topic right there. Call it "Stupid statement of the day". :eek:

Not a personal shot at you but sheesh.
 
Re: Oops...EMT offset on service

electricmanscott are you for real?!?

Just try to start arguing with an inspector and see where it gets you. Failing all your inspections! My point is, that it is better to make them happy then to piss them off arguing about how little about the code they actually know.

They all say how they enforce the code the same, but come on, if you really believe that then you are is green as it comes when it comes to working with inspectors.

When I was a journeyman electrician, I would have agreed with you 100%, I was about the code and the code only.

Now that I am a licensed contractor, I am about making the inspectors happy. It saves me money and time.

Give me a hard time if you wish, but if I were in the business of arguing with the inspectors, I would be loosing money and out of business.
 
Re: Oops...EMT offset on service

If anything my point is proven with this thread.

Two inspectors in San Francisco inspecting the same installation and I passed with die cast offset nipples and he didn't.

So tell me this, Is it about code or about making the inspectors happy when it comes to passing inspections?
 