all buildings are structures, not all structures are buildings, etc.
Which is the same as the NEC so I guess your point alludes me.
all buildings are structures, not all structures are buildings, etc.
Which is the same as the NEC so I guess your point alludes me.
the point is, nec should not use a broad brush in this case. an outdoor kitchen island is way different than say a barn/workshop structure in their use of power, etc. you cannot say why three BC's to a stand-alone island kitchen is not safe, you can only say it's not to nec current code.
eg; why not restrict stand-alone outdoor kitchens to no more than 60A worth of gfi'd ocpd w/ max ocpd size of 20A? three 20's, four 15's ? and allow feeder. something like that?
And it is also built or constructed if it is part of another structure.Well given your description the AHJ did not interpret the code they simply ignored it.
Clearly the kitchen is built or constructed.
earlier i asked why you thought multi BC's to a outdoor kitchen island was not safe, you said "its not nec compliant"I cannot say more than 3 circuits to any building or structure is unsafe so your point falls flat.
As far as your suggestions those are as arbitrary as any NEC codes
Sidebar: What's a Feeder?
Article 100 defines feeders as: “All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device.” The clumsiness of this wording makes this definition hard to follow.
Does it have at least 20 feet of rebar, if not it isn't required to be used as an electrode, that doesn't mean in some situations it may still have lower resistance then a rod though.but the mailbox post is in concrete, this ufer is better than a ground rod![]()
If GFCI is at the supply end of the circuit it could just be capacitive leakage of a long circuit causing the tripping and if the GFCI protection were moved closer to the end load the problem might go away.To summarize:
It is not yet clear if this tripping is because of low (near threshold) leakage current, so that random noise causes tripping, or if there is some intermittent event (say a defrost timer) causing much larger leakage current. It is not yet clear if the fault is in the circuit (say because of water ingress) or in the appliance.
The OP might benefit from splitting the loads into multiple circuits, because the ground fault leakage of each appliance and device is cumulative, so the fewer things connected to each GF sensor, the less the chance of a 'nuisance' trip.
If the OP decides to split the loads, it depends upon the specifics of the construction and the local understanding of what a _separate_ structure is to determine if this means a feeder and subpanel are required at each island.
-Jon
I see there was more posts I hadn't read at the time I posted this.And it is also built or constructed if it is part of another structure.
The question is whether it is a separate structure or not. Does it need to have a common roof or wall as another structure to call them same structure or can it just be connected by floor, walkway or other less discrete means and still be considered part of the main structure?
I don't think there is a single right answer.
almost all of my comments around ufers are in joking manner. if i use aDoes it have at least 20 feet of rebar, if not it isn't required to be used as an electrode, that doesn't mean in some situations it may still have lower resistance then a rod though.
its not attached = standalone structure, no ?? i not following your logic, or, is your logic in nec verbiage?I will just say that even though that kitchen is possibly somewhat "stand alone" it is probably more a part of the dwelling then it has a chance of even existing if there were no dwelling.
almost all of my comments around ufers are in joking manner. if i use aicon, i am likely joking around.
its not attached = standalone structure, no ?? i not following your logic, or, is your logic in nec verbiage?