I was told that we need to change the breaker ratings in "2BPP6" to match the Isc(31000A), and I'm having trouble understanding why? what would happen if they stay at the current 18KA rating.
Anything I could do to reduce Isc beside using fuses?
first,Replacing all the Underated CB's with properly rated CB's fixes that issue. Many thanks to all who helped with this issue.
2nd, protecting the XF 2ndary conductor.
1.What about the transformer 2ndary, say I have a similar XF(see first post) that runs 200 ft and terminates at an appropriately sized OCPD, is that against any rules?
if not what is protecting that conductor from XF to the OCPD?
Understand that I will also need GFPD too!?
2. say that I want to apply rule 240.92.C.1, adding a CB within 100ft of the XF, do I add the Ampacity of all the conductors leaving the transformer or just the Ampacity of the feed I'm concerned with?
ideally I would like to know what would be the correct installation of the XF with its proper OCPD and GFP/SCP(by applying 240.92.C.1, or GF relay)