Whenever the code requires overcurrent protection, is it assumed that these devices must have long-time (LT), short-time (ST) and instantaneous time-current characteristics?
I would think so since the definition for Overcurrent Protective Device, Branch-Circuit in Article 100 mentions the capability for providing protection over the full range of overcurrent between the OCPD's rated current and interrupting rating; but I cant find anything linking LT, ST or I characteristics to the terminology the NEC uses, i.e. Overload, Short-Circuit, Ground-Fault.
Why doesn't the NEC just simply state when LT, ST, I protection is required instead of stating short-circuit protection is required?
Note: The term short-circuit is ambiguous because it could be a combination of ST, I and/or GF time-current characteristics, leaving things open to interpretation...
Thanks in advance.
I would think so since the definition for Overcurrent Protective Device, Branch-Circuit in Article 100 mentions the capability for providing protection over the full range of overcurrent between the OCPD's rated current and interrupting rating; but I cant find anything linking LT, ST or I characteristics to the terminology the NEC uses, i.e. Overload, Short-Circuit, Ground-Fault.
Why doesn't the NEC just simply state when LT, ST, I protection is required instead of stating short-circuit protection is required?
Note: The term short-circuit is ambiguous because it could be a combination of ST, I and/or GF time-current characteristics, leaving things open to interpretation...
Thanks in advance.