Has the OP given enough input for that?
That is the question. What happened? Worn parts? Loose locknuts? Out of adjustment? Is this the way it has always worked? IDK. We never worked on it before.
Has the OP given enough input for that?
That is the question. What happened? Worn parts? Loose locknuts? Out of adjustment? Is this the way it has always worked? IDK. We never worked on it before.
Pay attention.But you said in an earlier post you replaced the offending switch and yet the issue persists!
What is the actual RMS input voltage? If you have a high input voltage to start with it may be easier to have little glitches that wouldn't cause troubles if input voltage were lower.Coil and control voltage is 120 v. The very simple suppressor is rated 130v. It may help the life of the control circuit contacts. The control is ran in the same conduit as the power to the motor for all of 50' and at may aid in the induction from that.
The DC BUS Voltage peak is 726
What is the actual RMS input voltage? If you have a high input voltage to start with it may be easier to have little glitches that wouldn't cause troubles if input voltage were lower.
If input voltage is over 500, maybe POCO has a voltage regulator problem, straighten that out and maybe your overvoltage fault issue goes away.
A transient
Any 3% line reactor?
Input line filter?Installed, see Post 1.
Input line filter?
Sent from my SM-G900V using Tapatalk
No.
Might be a better "next" than the braking resistor which will be fun to hang and protect. The last Input filter I used sat behind the drive, things could get tight.
Most 480 Vac VFD's will shut down on over-voltage when the capacitors hit 750 Vdc. ...
Reactors should help, but I can't remember, did you already try that?