I like marking my neutrals with ckt # in the panel, or at least pairing/taping each neutral to its respective blk, red or blu wire. I have seen issues before when removing or rearranging ckts in a crowded panel that the wrong neutral gets removed, wreaking havoc on another ckt.
We made a pull recently being careful to pair our neutrals all the way from load, through j boxes and to the panel. Boss came along and said it didn't matter, just cut and stuff them in the panel to connect later. He insisted, each wire has a neutral and it doesn't have to be marked.
I didn't turn this into a war with him but I think he is being very nearsighted, whereas he usually thinks ahead on more issues.
Feedback?
We made a pull recently being careful to pair our neutrals all the way from load, through j boxes and to the panel. Boss came along and said it didn't matter, just cut and stuff them in the panel to connect later. He insisted, each wire has a neutral and it doesn't have to be marked.
I didn't turn this into a war with him but I think he is being very nearsighted, whereas he usually thinks ahead on more issues.
Feedback?