The NEC does not allow an electrical panel on a stairway, but what about a stairway landing, if the clearance requirements are meet? Again code references would be appreciated! Thanks,
The NEC does not allow an electrical panel on a stairway, but what about a stairway landing, if the clearance requirements are meet? Again code references would be appreciated! Thanks,
240.24(F) Not Located over Steps. Overcurrent devices shall not
be located over steps of a stairway.
recently we had 100A circuit breaker installed in staircase. contactor advised us that inspector told him that c.b. should be in 2 hours rated enclosure. now I have doubts.
Sent from my Nexus 5 using Tapatalk
recently we had 100A circuit breaker installed in staircase. contactor advised us that inspector told him that c.b. should be in 2 hours rated enclosure. now I have doubts.
Sent from my Nexus 5 using Tapatalk
I agree, he's wrong.Ryan Jackson believes this installation violates 240.24(F). I disagree.
George I took the liberty to post the pic as it is a interesting question. When does a step become a step-- hold long/wide/etc.
There is no problem to solve until there are "steps". As long as the platform, in this case or landing in the OP, meets workspace requirements your good.(F) Not Located over Steps. Overcurrent devices shall not
be located over steps of a stairway
I agree, he's wrong.
There is no problem to solve until there are "steps". As long as the platform, in this case or landing in the OP, meets workspace requirements your good.
The NEC does not allow an electrical panel on a stairway, but what about a stairway landing, if the clearance requirements are meet? Again code references would be appreciated! Thanks,
George I took the liberty to post the pic as it is a interesting question. When does a step become a step-- hold long/wide/etc. View this larger with your browser to see details better. BTW, I can see Ryans response but without knowing the depth of the (step) I may challenge 110.26 but I suspect it is 36" or greater
![]()
I cannot be sure but if those psot are 6x6 then the depth from the building out is maybe 20" -- the depth measured is infront of the panel which if my assumptions are somewhat correct is about 12" for the walkway disconnects. IMHO that is a step not a landing.
The far left disconnect working space appears compliant.
It is not a stairway so it does not apply.![]()
Call it a step if you want but as worded it only applies to stairway steps.
I was going to ask about the same thing, how many steps needed before we have a stairway?Yeah you made that point LOL. I posted when you did and it was mentioned above. So when does it become a stairway-- 2 step?