Re: Parallel feeders single phase
With Karl's vast knowledge on the "effects" that may occur, it helps with a different perspective towards possible health affects and electronic interference considerations.
But back to the NEC for a minute.
Steve keeps mentioning "sheath", I do not see where sheath is mentioned. Maybe someone could point this out to me.
"300.3 Conductors.
(A) Single Conductors. Single conductors specified in Table 310.13 shall only be installed where part of a recognized wiring method of Chapter 3.
(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors
shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (4).
(1) Paralleled Installations. Conductors shall be permitted to be run in parallel in accordance with the provisions of 310.4. The requirement to run all circuit conductors within the same raceway, auxiliary gutter, cable tray, trench, cable, or cord shall apply separately to each portion of the paralleled installation, and the equipment grounding conductors shall comply with the provisions of 250.122.
Parallel runs in cable tray shall comply with the provisions of 392.8(D).
Exception: Conductors installed in nonmetallic raceways run underground shall be permitted to be arranged as isolated phase installations. The raceways shall be installed in close proximity, and the conductors shall comply with the
provisions of 300.20(B).
Concentrating on the exception seems to spell this out, that a PVC raceway is permitted.
I know this is usually installed in an open bottom switchgear, I have in the past been involved in a large IBM building where there were 20 sets of PVC raceways entering the building with isolated phases, making the termination a whole lot easier and a lot neater - especially because our company did the PM in this building/complex as well.
I agree with Roger that this may not be an everyday occurrance in our industry, but it can be installed this way, and if installed properly would be a safe installation.
This is also one of the reasons I love this industry: we have to constantly be aware of what we are doing and have new challenges everyday