Re: Parallel feeders single phase
Don
The way that I am reading article 300.3 is that I must follow what is outlined in (B) except as outlined in 1-3.
The only part that there seems to be a disagreement on is (3) so I will recap (B) then look a (3).
(B) states that paralleled conductors shall be contained within the same raceway
Now what does (3) say?
Conductors in wiring methods with a nonmetallic or other nonmagnetic sheath, where run in different raceways,?.. or cords, shall comply with the provisions of 300.20(B).
(we already have been told that if conductors are installed in a cable tray they must be bundled together in (1))
The key to (3) is the first eleven words which clearly state that (3) is talking a bout a cable or cord by the referral to sheath. The word sheath is used through out the code and is always referred to as inclosing conductors as outlined in the definition of MC cable.
Metal Clad Cable, Type MC. A factory assembly of one or more insulated circuit conductors with or without optical fiber members enclosed in an armor of interlocking metal tape, or a smooth or corrugated metallic sheath. Also see 332.2, 320.120, 334.2 ect
By using other articles of the code such as 310.4 (must be 1/0 or larger) and the articles on cable and cords we will find that there is a limited number of cords and cables that have a sheath and conductors 1/0 or larger.
A couple of the cords would be types EV, EVT, G, G-GC, PPE, SC, and W as outlined in 400.
The only cables that I am aware of are IGS, MC, MI, and SE
The way I am reading 300.3 is that if it is a conductor such as TW, THW, and THHW then it must comply with (B) but if it is enclosed in a sheath that is nonmetallic or nonmagnetic then it can be in a different nonmagnetic raceway and comply with 300.20 (B)
The only place that I can see where a conductor can be run in parallel in separate raceways is in the exception found under (B)(1).
We must keep in mind that a single conductor has insulation not a sheath. Therefore I cannot find in 300.3 (B) (3) where I am allowed to install a single insulated conductor such as TW, THW, THHW in parallel in different raceways.