You can’t simply up the SO cord to #4? That’s not an outrageous expense.
I'd bet the difference between 10/3 SO and 4/3 SO would be nearly 2.00 pr ft. difference.
Not that it matters as far as having to abide by the code.
JAP>
You can’t simply up the SO cord to #4? That’s not an outrageous expense.
yes, I figured that changing the plug was not legal regardless of whats been done in past.
As far as upping the cord.....that was my first choice however this is a relatively small skid (5'x5'x5' or somewhere around that)....it has piping all around it....the cord actually comes out of the bottom of the controls enclosure .....somewhere in the middle of the skid.......surrounded by piping, valves and framework.......did I happen to mention its a Pharmaceutical piece of equipment and everything is stainless? There really is no easy access to the strain relief.....from either the outside of the enclosure or the inside....cramped doesn't actually do it justice.....and once inside the enclosure it (the cord) snakes behind some wireway and components, around the enclosure until it lands on a small rotary disconnect.....its not rated for 60a either.....so I'd probably need to swap that out also.....and lets not forget the wiring from the disconnect to the first current limiting device.....that doesn't meet 60a distribution requirements either. And thats bundled inside the wireway and also snakes around the enclosure. (don't ask me why, I didn't build the thing)......so it gets a bit involved to swap the cable.
My answer was to add a small enclosure with a MCCB and an integral handle and disconnect, rated at 30a to the machine.....I'd wire 4/4 cord from the supply side of the MCCB to a 60a plug that matches the wall receptacle.....then I'd wire the existing cord already installed to the load side of the MCCB. Thats a bit more than $300 for 15' of SO Cord and a hubbel plug.
And did I forget to mention that they have a dozen or so other pieces of equipment where someone simply swapped the plug.....I've already indicated to my customer that I don't believe they don't meet code.
thanks, bob :roll:
So you've got a Frankenstein machine from Bulgaria and you want the NEC to be a substitute for manufacturer specs, or guidelines. That's not what the NEC is for. The NEC tell us what to do to safely bring power up to the spot on the wall where the machine plugs in.yes, I figured that changing the plug was not legal regardless of whats been done in past.
As far as upping the cord.....that was my first choice however this is a relatively small skid (5'x5'x5' or somewhere around that)....it has piping all around it....the cord actually comes out of the bottom of the controls enclosure .....somewhere in the middle of the skid.......surrounded by piping, valves and framework.......did I happen to mention its a Pharmaceutical piece of equipment and everything is stainless? There really is no easy access to the strain relief.....from either the outside of the enclosure or the inside....cramped doesn't actually do it justice.....and once inside the enclosure it (the cord) snakes behind some wireway and components, around the enclosure until it lands on a small rotary disconnect.....its not rated for 60a either.....so I'd probably need to swap that out also.....and lets not forget the wiring from the disconnect to the first current limiting device.....that doesn't meet 60a distribution requirements either. And thats bundled inside the wireway and also snakes around the enclosure. (don't ask me why, I didn't build the thing)......so it gets a bit involved to swap the cable.
My answer was to add a small enclosure with a MCCB and an integral handle and disconnect, rated at 30a to the machine.....I'd wire 4/4 cord from the supply side of the MCCB to a 60a plug that matches the wall receptacle.....then I'd wire the existing cord already installed to the load side of the MCCB. Thats a bit more than $300 for 15' of SO Cord and a hubbel plug.
And did I forget to mention that they have a dozen or so other pieces of equipment where someone simply swapped the plug.....I've already indicated to my customer that I don't believe they don't meet code.
thanks, bob :roll:
So you've got a Frankenstein machine from Bulgaria and you want the NEC to be a substitute for manufacturer specs, or guidelines. That's not what the NEC is for. The NEC tell us what to do to safely bring power up to the spot on the wall where the machine plugs in.
Personally, I don't see a problem with using the smaller cord. Smaller cords are used on bigger circuits all the time and the way you describe it the machine is going to protect the cord from overload so the 60A breaker is nothing more than short circuit ground fault protection. That's the same thing we do with motor circuits and breakers all the time.
And ignore 240.10?.
JAP>
My answer was to add a small enclosure with a MCCB and an integral handle and disconnect, rated at 30a to the machine.....I'
You are asking the NEC for something that it's not written for. The NEC is a safety standard for premisis wiring, it's not a guideline or standard for manufactured equipment.....So if you can point to something in the code that indicates in some fashion this would be allowable I'll be more than happy.
thanks, bob :huh:
Absolutely, or tap the 60a circuit and use an inexpensive breaker or fused disco for the lesser circuit,Get rid of the 60 amp receptacle and set a subpanel in it's place to reefed a 60 and 30 amp receptacle below it.
but if you can use 20 amp circuits on fifty amp stove breaker to feed oven and stovetop rather than full range,
I was always taught that unless you can put a fuse at the plug to protect the voltage to the wire, the wire must be rated for the voltage of the plug. But, did not see that in the codes I just read as noted above. So, not sure. Then again, how do you wire a 20 amp stove and a 20 amp oven from a 50 amp stove outlet and it be fine?
Sorry you got irked. It wasn't my intention to be irksome. It was meant to give some perspective that the NEC is a resource but it's not all encompassing. I am irked that every three years I have to put up with a bunch of code changes that don't have anything to do with the original scope of the NEC.this irked me so my reply is directly to ActionDave.
It was a whimsical description, not a dismissive one. It was based on your posts that basically said it's a complex machine from overseas.First off, I doubt its a Frankenstein machine.
Second, I wasn't looking for the NEC to replace any manufacturers specifications. I was simply asking a straight code specific question. And I doubt that your response would apply if the manufacturer was doing something YOU knew didn't meet code, or wasn't safe
case in point, if you were asked (normally by the end user not the manufacturer) to wire a motor in a Classified area, and the manufacturer said you don't need to use seals, would you do so and simply shrug it off. I'll make it easier, the motor goes from their control panel in a non classified area, into the classified area. And the motor isn't XP either. (the mfg tells you they've never had a machine issue) According to you, your obligation ends at the power feed to the control panel. Everything else is up to the mfg of the equipment. I'll remind you (as some reading this may not be aware) that as a licensed electrician, and working for the end user, you have a legal obligation not to do whats potentially wrong, and possibly dangerous. I hold off on telling you, you might also have a responsibility for not allowing it to be installed in that fashion by anyone.
I am aware that if I drop the feed to 30a I'm ok. I'm aware that if I put in a sub-panel I'd be ok. The mfg put a 30a plug on the machine so apparently they wanted a 30a feed circuit. Still didn't really answer my question would it be acceptable practice to put a 60a plug on the machine.
From the responses I got, as well as specific issues in the NEC code, I would make an acceptable argument that its not. I found no one that could make any code based argument that it would be.
thanks, bob:blink:
The mfg put a 30a plug on the machine so apparently they wanted a 30a feed circuit. Still didn't really answer my question would it be acceptable practice to put a 60a plug on the machine. From the responses I got, as well as specific issues in the NEC code, I would make an acceptable argument that its not. I found no one that could make any code based argument that it would be.
thanks, bob:blink: