A 702 installation is a complete installation. What you propose is not a complete 702 installation.
702.1 Scope.
The provisions of this article apply to the
installation and operation of optional standby systems.
The systems covered by this article consist of those that are permanently installed in their entirety, including prime movers, and those that are arranged for a connection to a premises wiring system from a portable alternate power supply.
702.11 Portable Generator Grounding.
(A) Separately Derived System. Where a portable optional standby source is used as a separately derived system, it shall be grounded to a grounding electrode in accordance with
250.30.
(B) Nonseparately Derived System. Where a portable optional standby source is used as a nonseparately derived system, the equipment grounding conductor shall be bonded to the system grounding electrode.
110.3(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
FTCN.GuideInfo
Engine Generators for Portable Use
[Engine Generators] Engine Generators for Portable Use
445.1702.10(A)702.10(B)445.1702.10(A)702.10(B)445.1702.11(A)702.11(B)
GENERAL
This category covers internal-combustion-engine-driven generators rated 15 kW or less, 250 V or less, which are provided only with receptacle outlets for the ac output circuits. The generators may incorporate alternating- or direct-current generator sections for supplying energy to battery-charging circuits.
When a portable generator is used to supply a building or structure wiring system:
1. The generator is considered a separately derived system in accordance with ANSI/NFPA 70, "National Electrical Code" (NEC).
2. The generator is intended to be connected through permanently installed certified transfer equipment that switches all conductors other than the equipment grounding conductor.
3. The frame of a certified generator is connected to the equipment-grounding conductor and the grounded (neutral) conductor of the generator. When properly connected to a premises or structure wiring system, the portable generator will be connected to the premises or structure grounding electrode for its ground reference.
4. Portable generators used other than to power building or structure wiring systems are intended to be connected to ground if required by the NEC.
PRODUCT IDENTITY
The following product identity may appear on the product:
Engine Generator for Portable Use
You make you application for a permit for what? If it is for an optional standby system then I will see that complete system to ensure that what is being installed complies with the adopted laws of my state. In order to comply it must meet 110.3(B) and be listed. If it is listed it will be built to the compliance to UL Standard 2201 and the neutral will be bonded to the frame of the generator.
You are the one who applied for the permit and you will be the one I will be asking about the generator. Should you decide to take your personal generator for inspecting purposes and then remove the generator I promise that you will have a chance to explain your actions to your licensing board.