mistermudd
- Washington State
300.3 all single conductors must be installed where part of a recognized wiring method.
			So.....if I'm running EMT and no EGC, then the fitting would be my ground path and by this same logic the screws that tighten that fitting would have to be accessible?
Once you're back-fitted box has been rocked over, you're gonna have to bust up the drywall to tighten it up if it comes loose.
OUCH! Think outside that box. A drill/tap can fix the problem quite easily without tearing up drywall.
IMO the code requires the EGC connection to remain accessible and protected from damage.
Beyond that ...........
- Running the EGC outside the box looks hack
- Our guys seem to be able to quickly install the pigtail inside the box.
- If the inspector does have an issue with it your going to burn up a lot of time fixing it.
If you don't have the time to do it right the first time, when will you have the time to do it right?
So if you run into a situation where the ground screw, which is loose and installed from the outside of the box, you are going to remove the drywall to fix the problem!? You're not going to get many return calls that way. I'll grab my drill and tap, make a new threaded hole and install it correctly and move on to the next job. I'll get the next call out to fix any problems they may have.
Nec 2008 314.29
Have you ever noticed how electricians like to argue a point even when they(myself included) know it is a bad idea and would not do it that way.
:grin::grin:OUCH! Think outside that box. A drill/tap can fix the problem quite easily without tearing up drywall.
The switch box is 3-1/2" deep. With a cordless drill and standard driver bit, the outside method is a lot faster.
I guess nobody else asked this question, but why are you using sectional device boxes in the first place?This is 2009, not 1959.
	Is it legal by the NEC to install the pigtail with the 10/32 screw on the outside of the switchbox?
Is it legal by the NEC to install the pigtail with the 10/32 screw on the outside of the switchbox? I realize the screw will not be serviceable, however, it is not a grounding electrode conductor (the GEC is the only bonding I could find that does require serviceability). The apprentice could install these much faster from the outside.
300.3(B)(2)... Equipment bonding conductors shall be permitted to be installed on the outside of the raceways in accordance with 250.102(E).
250.102(E) Installation. The equipment bonding jumper shall be permitted to be installed inside or outside of a raceway or enclosure.
Several months ago, I installed some troffers that had make up plates with the ground screw or bonding jumper exposed like my switch box picture. An old hippy coworker recalls running bonding jumpers on the outside of greenfield to motors and XFMR's back in the early 70's. Good ideas always come back into fashion. :grin:
QUOTE]
In all of those applications the final connections remain accessible.
Then there is the one that hasn't been commented on about your picture,there is no way that green wire has a bending radius that meets code.
300.34 Conductor Bending Radius.
The conductor shall not be bent to a radius less than 8 times the overall diameter for nonshielded conductors or 12 times the overall diameter for shielded or lead-covered conductors during or after installation. For multiconductor or multiplexed single-conductor cables having individually shielded conductors, the minimum bending radius is 12 times the diameter of the individually shielded conductors or 7 times the overall diameter, whichever is greater.