Knuckle Dragger
Master Electrician Electrical Contractor 01752
- Location
- Marlborough, Massachusetts USA
- Occupation
- Electrical Contractor
What it allows the car owner to do is program the EV to draw what is allowed for the that particular branch circuit that is installed.But that doesn’t allow you to downsize the branch circuit. Per 625.42, in order to use a branch circuit less than the maximum EVSE rating, it must be limited by a hardware setting not easily accessible to the user.
There is also an allowance to use a software limit, but it must be password protected with the password only available to qualified personnel. But I can’t imagine this in a residential installation.
If it's a 50amp rated branch circuit program to draw 40 amps.