Excellent article!!! Thanks!
The residential breakers available at the present time are are in no way capable of responding to arcults. In addition the last time that I checked when comparing a standard residention breaker SqD's has a std breaker and a high mag version available as an option. When compared to Eaton (C-H), Eaton has a std breaker and a low mag breaker as an option. As such if you order a common SqD and Eaton panel you will actually a low mag in the SqD and a high mag in the Eaton panel.
The SqD std panel may be closer to the goal of responding to arc faults.
A look at an actual TC curve for the residential breaker will shead some light on them. They are crude.
Solenoid technoligy has been used for years with MCPs for 3-150a where 100% of the current goes through the coil of the solenoid and they are adjustasbel to correspond tho the FLA of the motor. As such the size on the conductor of the coil must be capable of handing the current. (With a 3/4 or 1" per pole breaker even be suitable for a 9 turn turn solenoid? Maybe.a breaker similar to the UL1077 devices?) The solenoid is adjustable to corispond to a motor's FLA to respond to a phase to ground winding fault. MCPs are designed based upon their quick response to such faults to limit motor damage and prevent fires.
In contrast the common mag element of a residential breaker I often call a clapper type which simply pulls a trip against the conductor when the current reaches a given magnitude. The simplistic design does not lend itself to being "fine tuned" that is to be calibrated to a level that would respond to arc faults. It is useless. As I recall the manufacturing tolerernces are +-20% of their published values in order to pass inspection. I have a sales sample an the original Westinghouse BR 1p 20at breaker but instead of a black molding it has a clear see through enclosure that you can actually see the thermal and mag elements as well as the trip mech. There is not much to be "fine tuned.".
Yes, without using electronic technology solenoids are the best answer as they have the capability of being more closely calibrated and the UL1077 supplimentasry protectors have been available with this technology for some time now. I discovered that EATON has the FAZ-NA available that may fit this requirement. Other manufactures may have a similar breaker.
This is a short excerpt of Eaton's description and its UL489 device is interesting:
-Current limiting design provides fast short-circuit interruption that reduces the let-through energy that can damage the circuit
-Thermal-magnetic overcurrent protection
-Three levels of short-circuit protection, Categorized by B, C and D curves
-Trip-free design. Breaker can not be defeated by holding the handle in the ON position.
These are available with 3different curves. The B curve seems to be the best.
FAZ-NA—B curve (3–5X In current rating) ............................................... FAZ-NA—C curve (5–10X In current rating)
FAZ-NA—D curve (10–20X In current ratng)
Why this technology isn't used for the common residential breakers is a good question. The