No problem. The key is a panelboard is mounted in a cabinet. You are free to splice in a cabinet of course.
So, this circuit is getting power from the blue wire? But it's not getting a neutral from the same panel? Maybe I am not seeing what I am looking for in the picture.
If these conductors are feeding thorough the panel then it's required to labeled as such.
If these conductors are feeding thorough the panel then it's required to labeled as such.
I only see black and white in and out, with only EGC's on the grounding bus.The twisted together neutrals under the same setscrew is a deal breaker but that isn’t the question.
I only see black and white in and out, with only EGC's on the grounding bus.
Oh, those neutrals. I've only been looking the two NM cables at the bottom.look at the neutral bar to the lower right. Near the breakers The whites are twisted together and put under the same screw.
Depends on the length, IIRC, >10’. IDR the article...I’m looking.That piece of Romex coming out of the bottom of the panel going into that piece of rmc used as a sleeve
if I'm not mistaken is that sleeve required to be bonded?
Sent from my SM-G965U using Tapatalk
The twisted together neutrals under the same setscrew is a deal breaker but that isn’t the question.
2 cables into bottom of enclosure - right cable from a breaker in a neighboring enclosure, then routed here and spliced, and back out (left cable at the bottom to its destination (via conduit). Is splicing proper in this manner?
Regarding your specific question, the EGC's should be spliced together