Proper way to splice?
tonype
New Jersey
2 cables into bottom of enclosure - right cable from a breaker in a neighboring enclosure, then routed here and spliced, and back out (left cable at the bottom to its destination (via conduit). Is splicing proper in this manner?
If these conductors are feeding thorough the panel then it's required to labeled as such.
look at the neutral bar to the lower right. Near the breakers The whites are twisted together and put under the same screw.
Oh, those neutrals. I've only been looking the two NM cables at the bottom.
It's doubly ridiculous that was done with all of those empty terminals. :roll:
That piece of Romex coming out of the bottom of the panel going into that piece of rmc used as a sleeve
if I'm not mistaken is that sleeve required to be bonded?
Sent from my SM-G965U using Tapatalk
The twisted together neutrals under the same setscrew is a deal breaker but that isn’t the question.
and (2) cables in one connector, and surface run cable- but I guess both those fly in some ahj's. is there only (2) black wires under the yellow? it looks like there is another (2) blacks doing something weird on the bottom... cant see. anyhow, if surface is ok its not too hard to set a couple of boxes and get it out of there...
Regarding your specific question, the EGC's should be spliced together just like the hot and neutral conductors from those two cables and a notation on the panel that there are feed through conductors. The label requirement was added in the 2011 NEC so it might not apply to your installation if it was done before the adoption of the 2011 NEC. As stated there are other issues.