What are the pros and cons of using 120 volts or 240 volts to power residential floor heat? The resistants' is about 22 ohms. I was just curious, the prints say 120. I thought it would heat faster on 240.
180507-2243 EDT
What stray magnetic field is created?
.
That would entirely depend on the design of the thermostat. Most electronic ones would need the neutral just to power the electronics even if they don't switch the neutral.On 120 , Do you put the neutral on the thermostat, too.
Line 1 Black Line 2 white?
Or do you make the neutral by-pass the thermostat?
1) the total wattage is not the only thing in this story. 0.25watt on a surface area of 0.01in^2 will about burn you very fast. 4000watt over say 200sq.ft. is 20w/ft^2, which is a decent amount of heat. but if ambient is say -20F then 20w/ft^2 may only keep the bottom of bare foot warm. power flux and operating temps and room sizing are important. but remember, even in a room that is 20ft high, you only need to heat and cool to about the 1st 7ft, because we rarely hang out in any room above 7ft, etc.180507-2243 EDT
At 120 V 22 ohms is about 654 W, and four times this at 240. Neither will do much heating.
What stray magnetic field is created?
.
That would entirely depend on the design of the thermostat. Most electronic ones would need the neutral just to power the electronics even if they don't switch the neutral.
Latest NEC and dwellings - 120 volt needs to be AFCI protected in most instances.
Which heats faster - well if you put in say 1000 watts of heat - won't matter 1000 watts is 1000 watts, just draws twice as many amps at 120 then at 240, still draws 1 kilowatt hour for every hour it runs.
Now if you put in 1000 watts of 120 volt rated heat cable and apply 240 volts to it - it will draw 4000 watts - will heat much faster - will likely burn out in no time also.
120v is "safer" (lower voltage) than 240.
It’s still 120 volts to ground. There’s virtually no difference in safety. Voltage drop is substantially reduced at 240 though
Sent from my iPhone using Tapatalk
For the same wattage element the current will be 1/2 for the 240V circuit compared to the 120V circuit. That means twice the voltage drop in the supply wiring (if same size wire) and the power wasted in that wiring will be four times that in the 240V circuit.or 240 end to end.
voltage drop should be 120v end to end if its on 120v
voltage drop should be 240v end to end if its on 240v
perhaps i just not getting what you mean by voltage drop
2) AC60Hz, a stray alternating magnetic field is created 60x/sec. you have amps, you have EM fields. what it looks like in spatial depends on if its homogeneous heating mat, or a wire that loops around.
Yes, on the safety aspect. And yes, lower voltage drop if you used the same size conductor. OTOH, you might choose to use smaller conductors and save cost.It’s still 120 volts to ground. There’s virtually no difference in safety. Voltage drop is substantially reduced at 240 though
Has to be something grounded (with low enough resistance) in close proximity to fault to, if not the conductive portion of element likely heats up to a point it melts somewhere and eventually leaves you with open circuit condition.If you apply twice the voltage to a resistive element it will likely break down the insulation, cause a ground fault and possibly start a fire.
Sent from my iPhone using Tapatalk
but OP said its not fixed wattage, more like fixed load.For the same wattage element the current will be 1/2 for the 240V circuit compared to the 120V circuit. That means twice the voltage drop in the supply wiring (if same size wire) and the power wasted in that wiring will be four times that in the 240V circuit.
Sent from my XT1585 using Tapatalk
well, i suspect not. EM fields attenuate as a function of radius. the EM fields from each conductor of the do not hit each other at exactly |B|-|-B|, etc. nearly cancel each other out depending on geometry of the coax, is a better answer. would this net be of concern, likely not. ~5A on one wire has net that would not likely be of concern, but there is net. :thumbsup:Aren't these floor heating elements coaxial, with the current returning on the outer braid so both connections are at one end? That's what I've seen. That design has no net magnetic field outside the cable itself.
A resistance value was all he gave.but OP said its not fixed wattage, more like fixed load.
A resistance value was all he gave.