Pull Box, 36" x 36" w/480V motor branch circuit - Article 110.26 and T110.26(A)(1)
I'm not sure how to call this one: in reviewing the plant this am, (under construction) I noticed a large, Nema 4X Stainless Steel enclosure, 36" x36" x 8" deep, installed between two units - the distance from the front of the Enclosure to the adjacent structure was less than 20 inches - hardly enough working space, even for a midget electrician.
After reviewing the drawings, I noticed the cable did not actually terminate within the enclosure, it was simply pulled through in a giant horseshoe loop - i.e. in the bottom/out the bottom.
This is horrible design, but is it a Code violation?
I'm not sure how to call this one: in reviewing the plant this am, (under construction) I noticed a large, Nema 4X Stainless Steel enclosure, 36" x36" x 8" deep, installed between two units - the distance from the front of the Enclosure to the adjacent structure was less than 20 inches - hardly enough working space, even for a midget electrician.
After reviewing the drawings, I noticed the cable did not actually terminate within the enclosure, it was simply pulled through in a giant horseshoe loop - i.e. in the bottom/out the bottom.
This is horrible design, but is it a Code violation?