pics of an unusual pull at link, thanks to George. :wink:
http://picasaweb.google.com/lh/sredi...rgK&feat=email
The elctrical contractor is using their truck to pull wire through conduit. They are attaching nylon rope to the end of the wire, running the rope over a pully then attaching the rope to the truck to pull the wire. Is this within NEC code.
Thank You,
Michael Ripoll
There is not a code issue here, but some serious safety issues. You do not have near as much control when using a truck as when using a tugger. You have a lot more exposed rope when using a truck. The rope is probably not a rope suitable for pulling cable. It is likely a dynamic rope that will store a lot of energy that will be released if the rope breaks and a dynamin rope tends to pull in "jerks" that can injure the cable feeder person. One of the Greenlee tugger manuals says for a 5,500 pound rated tugger a dynamic rope stores enough energy to launch a standard size car 14 stories. Even the correct rope stores enough energy to send that same car two stories.
Ok. Where do we find the tensile strength of various conductors?If you're concerned about excessive pulling force use a rope that will break before the conductors can be damaged.![]()
Ok. Where do we find the tensile strength of various conductors?![]()
Ok. Where do we find the tensile strength of various conductors?![]()
(BTW I am talking power conductors, communication cables are another story altogether)