crossman
Senior Member
- Location
- Southeast Texas
One consideration concerning using EMT (or other metallic wiring methods ) as the EGC is the construction of the building itself. If it is all metal structure with metal columns and bar joists, and the conduit is strapped/tie wired to the metal, with multiple conduits from the panels, we end up with a bunch of parallel paths for ground fault current, which is a good thing. The overall impedance of multiple ground fault paths will be lower than a single path.
Throw in the building steel itself bonded at the service, also possble metallic water piping /sprinkler piping/other piping attached to the building structure and/or bonded, the whole thing makes up multiple paths for ground fault current. In this case, a loose EMT coupling screw or corroded fitting will make no difference because of all the other paths available.
Now, with a wood structure, the single EMT path becomes critical for a good ground fault path.
Throw in the building steel itself bonded at the service, also possble metallic water piping /sprinkler piping/other piping attached to the building structure and/or bonded, the whole thing makes up multiple paths for ground fault current. In this case, a loose EMT coupling screw or corroded fitting will make no difference because of all the other paths available.