chris kennedy said:
I'm starting to think these threads (EGC in EMT) should go join "Ground up or down"
I don't see any benefit.
Hoppy Holidays All:smile:
I see a benefit, the benefit is that people are learning what the NEC does and does not require.
I often see links in these threads that show without a doubt that properly installed metal conduit systems have less impedance the any wire EGC you would install inside them.
An example where I intentionally left out an EGC to save money.
I had to run a 480 volt, 1,200 amp feeder about 400' through a steel frame building.
I ran three 3" EMTs using steel set screw fittings each tightened with a socket and ratchet, every 10' the EMTs sat on a Unistrut rack with each uni-strut clip also securely fasted, with each rack secured to the steel building structure every 10'.
That group of conduits impedance would most definitely be below the impedance of the EGC that would have been required. Do I have the least bit of worry that it is not 'grounded enough' nope, no thought of that at all.
Besides about 1,300' less 3/0 CU the EMT size was reduced and the labor for pulling and terminating was reduced. (It was design build)
I also used the building steel as a grounding electrode jumper to save a 400' run of 3/0 copper to water pipe from the service.
Knowing the code is power, when we choose to use that power is up to each one of us and the prints.