Just for my information, if it was a parallel run of 3 conduits, there would actually be three 3/0s in parallel for the EGC. For the calculations that Don did, wouldn't the other two 3/0s contribute to the grounding path?
In other words, at 12000 amps, a 3/0 is good for 50 feet? But what about the other parallel 3/0s? Shouldn't they be considered to carry some of the fault?
In other words, at 12000 amps, a 3/0 is good for 50 feet? But what about the other parallel 3/0s? Shouldn't they be considered to carry some of the fault?