Because it's made for flex. Use a male threaded PVC adapter glued on>threaded coupling>EMT connector.Any reason to not use a set screw adapter typically used for flex,
Why not a female PVC adapter and a connector?Because it's made for flex. Use a male threaded PVC adapter glued on>threaded coupling>EMT connector.
-Hal
Do you mean the threads have not been evaluated for mechanical connectivity as opposed to electrical/ground continuity or is watertightness the issue?Note both of these ideas are not acceptable to some AHJs as the male threads of the connector have not been evaluated for use with female threads.
358.6: "EMT, factory elbows, and associated fittings shall be listed."But if listed materials are not required
That looks like its for ENT not PVC.View attachment 2582510This is listed for the purpose
The EMT would be bonded by a proper EMT fitting at the other end if terminated at a bonded enclosure and would only need a bonding bushing if the general rules for needing additional bonding methods call for it. The PVC would never need a bonding bushing.Would require a grounding bushing when terminated, depending. Use the flow chart for grounding bushings.
The simply have not been evaluated for any use with a fitting having female threads. The have only been evaluated for use with locknuts.Do you mean the threads have not been evaluated for mechanical connectivity as opposed to electrical/ground continuity or is watertightness the issue?
The page specifically said Schedule 40 or Schedule 80 PVC.That looks like its for ENT not PVC.
I didn't know a strictly mechanical connection need to be evaluated.The simply have not been evaluated for any use with a fitting having female threads. The have only been evaluated for use with locknuts.
In this case, no grounding bushing is required on the PVC transition end.Would require a grounding bushing when terminated, depending. Use the flow chart for grounding bushings.
90.4(B) and 110.2. It's always up to the AHJBut if listed materials are not required isn't it up to the AHJ.
Is a male PVC adapter listed for connection to a threaded steel coupler? And is an EMT connector listed for connection to a threaded coupler?Because it's made for flex. Use a male threaded PVC adapter glued on>threaded coupling>EMT connector.
-Hal
YesIs a male PVC adapter listed for connection to a threaded steel coupler?
NoAnd is an EMT connector listed for connection to a threaded coupler?
So I didn't put this in the OP, but I need to transition from PVC to metal raceway in a solar PV DC circuit where Art 690 requires metal raceway when run inside buildings. So trying to transition as soon as the PVC comes through the drywall, so there is little to no PVC visible. The flex to emt coupler achieves that and fits like a glove.90.4(B) and 110.2. It's always up to the AHJ.
If the fitting is secure and everything is effectively bonded, I, as an inspector, don't get too wound up about these things. But that is just how I roll, not how other inspectors are or should be.
No, many inspectors let this go or don't know. Most won't let what OP posted go though.Is a male PVC adapter listed for connection to a threaded steel coupler? And is an EMT connector listed for connection to a threaded coupler?
No, I'm an electrician, not a plumber.Is that PVC water line?