Hello everyone,
Long time follower, first time posting.
I've been in the field for over 20 years, but mostly industrial/commercial. I'm getting a lot of contradictory replies from license holders regarding the proper breaker for an electric range, and can use some assistance.
Nameplate is 208v, single phase, 91amps, 17.3kw
Using table 220.55, column C I'm seeing a demand factor of 10,260kw.
When I calculate that by 208v, I'm getting 48amps.
Would I be safe to use a 60amp breaker?
The replies I've gotten have ranged from
60-->80->125amps.
Thanks in advance.