I’m with you on most of your calculations, but not all of it. This is because, if you drop the fraction 0.3 kVA at the beginning of the equation before calculating you receive a different answer than if you drop a fractional ampere 0.3 or at the end of the equation. Also 0.3 kva is actually 300 Va or 300VA / 208 E (single phase?) = 1.44 amperes and over 1 ampere which you do not dropTherefore, your range is well over that rating so we must apply Note number 1of that table.
Referring again to that note, it says to increase Column C by 5 percent for every additional kilowatt of rating or major fraction thereof for the individual ranges exceeding 17.3 kW. (drop the 3 fraction).
Therefore, 17.3 KVA = 17,300 - 12,000 = 5,300 VA / 1,000 VA = 5.3 x 0.05 (5%) = 0.265% increase or 1.265 multiplier for column C value of 8,000 VA (1 range) = 10,120 VA / 208 E (volts) = 48.65 i amperes. Since end result 0.65 i amperes is larger than 0.3 or even half an ampere, i think its best to round up to 1 ampere for a total of 49 amperes
People on this post have told me to not consider ranges as a continuous load because the burners are cycled. With this in mind you would not need to multiply this by 125% to size the branch circuit for the appliance but what about conductor correction for ambient temperature and those if current carrying conductors in a conduit exceed 3 or more?
what’s confusing is that the book from what I remember said both the branch circuit shall be the name plate rating 17,300 VA (larger wire) = 83.17 i but also says the branch circuit shall be permitted to be based on the table 8,000 VA for 1 range plus 5% increase to column C over 12k, which yields a smaller 49 I ampere conductor I calculated