Hello everyone,
Long time follower, first time posting.
I've been in the field for over 20 years, but mostly industrial/commercial. I'm getting a lot of contradictory replies from license holders regarding the proper breaker for an electric range, and can use some assistance.
Nameplate is 208v, single phase, 91amps, 17.3kw
Using table 220.55, column C I'm seeing a demand factor of 10,260kw.
When I calculate that by 208v, I'm getting 48amps.
Would I be safe to use a 60amp breaker?
The replies I've gotten have ranged from
60-->80->125amps.
Thanks in advance.
Hello, retnoc.
Here's the way to calculate your household electric range.
Using the 2023 NEC Code. Section 220.55 refers to T.220.55 " ....for household demand factors and loads..."
See note Number 1 of that table for ".....Over 12 kW through 27kW...." You stated only one range at 12.3kW
Therefore we will have to use Column C titled...
Maximum Demand (kW) (see notes) Not over 12 kW.
Therefore, your range is well over that rating so we must apply Note number 1of that table.
Referring again to that note, it says to increase Column C by 5 percent for every additional kilowatt of rating or major fraction thereof for the individual ranges exceeding 17.3 kW. (drop the 3 fraction).
Thus, 17 kW - 12kW = 5 kW at 5 percent 5% x 5Kw = .25 ( 5% for each Kw over 12kW per note number1)
One range from T.220.55 and column C is at 8 Kw.
Must increase that 8 Kw x .25 so multiply the 8 Kw x 1.25 = 10,000 Va or kW or 8,000 x 1.25 = 10,000 W or Va.
I put a number 1 in front of the .25 (1.25) thus the 1 is a hundred percent of the 8kW from Column C plus the 8,000 watts rating for one range.
Obey Ohm's Law, 10,000 watts/ 240 volts =41.66 amps or 42 amps.
Using
romex or type NM and the ampacity from T.310.16 in the 60 degree column it requires a 6 AWG at 55 amps.
Table 240.6(A) list a standard size to be a standard 45 amp OCPD. Check Section 334.80
Ampacity.
As to why I did that, take a moment and read that section for using the 60 degree column of T.310.16, the final ampacity for type NM.
Thanks for reading
TX+ MASTER #4544