Does anybody know if there is a new code that says you cannot put the range plug behind the range
Does anybody know if there is a new code that says you cannot put the range plug behind the range
But, the OP could be referring to a 120V receptacle for the ignitors and controls for a gas range. There were changes to the code that now require that to be GFCI'd and if you use a GFCI receptacle it has to be accessible.
I want to add that a locking device is only required if the breaker or switch is not in sight of the appliance.
I have never once seen these rules enforced or had it even mentioned by any inspector...neither the AHJ nor home inspector. I guess they assume the range drawer space is always open at the back of all ranges...definitely not the case. If the drawer is a "warming drawer" which is a fairly common feature, it's unlikely the back is open.
IMO the same disconnect rules should apply to refrigerators (422.33(A) and 422.31) since the accessibility of the plug is the same or even more difficult with refrigerators. But that's another one I have never seen enforced or mentioned by inspectors.
No, but they can wreak havoc with GFCI's as they spark to ground....gas strikers don't need much power.
No, but they can wreak havoc with GFCI's as they spark to ground.
Going to play devils advocate here and ask what the OP considers a "range plug". If it is the 40A/240V supply for an electric range then the previous replies about a removable drawer are correct.
But, the OP could be referring to a 120V receptacle for the ignitors and controls for a gas range. There were changes to the code that now require that to be GFCI'd and if you use a GFCI receptacle it has to be accessible.
-Hal
I'm curious.
What does the electronics that produce the spark to ground have anything to do with affecting the operation of a GFCI ?
JAP>
I believe that, because the igniter sparks to the chassis of the range, anything less than perfect electrical isolation of the power supply can be seen as a low-current fault to ground.What does the electronics that produce the spark to ground have anything to do with affecting the operation of a GFCI ?
Warming drawers are usually removable and accessible to the plug area, at least on the ones I have been looking at lately. Even the gas ones.
What code states you need a GFCI for gas range receptacle? I think you thinking if its with in 6’ from the edge of the sink, it needs GFCI protection but I don’t think so if not.
IMO the same disconnect rules should apply to refrigerators (422.33(A) and 422.31) since the accessibility of the plug is the same or even more difficult with refrigerators. But that's another one I have never seen enforced or mentioned by inspectors.
N 422.5 (B) Type. The GFCI shall be readily accessible, listed, and
located in one or more of the following locations:
cover all concerns if a small kitchen sub panel is w/in sight of the kitchen (lockable) & full of DF'swhere the switch or circuit breaker is within sight from the
appliance or is lockable in accordance with 110.25.