hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
What is in the photo to use as a reference to determine the size of anything?
We have no idea what the width of the trench is, and have no known objects to compare sizes to. Asking the OP what size the rebar is, is acceptable, but telling him what size it is with no supporting evidence is not right.
I believe if we look at the tie wires if they are common bailing wire then these rebars are at least ?" in diameter, the vertical rod looks as if it is a little larger.
I see no problems here, and the picture is exactly what I see a lot of the time.
The vertical pieces are driven into the ground, not for use as grounding electrodes, the concrete guys could care less about that, they are used both as vertical reinforcement of the concrete and as a place to tie the horizontal bars to for positioning them where they want them in the pour. IMO your GEC needs to tie to a full 20 foot piece of bar, meaning that it can not tie to any of the vertical bars if they are less than 20 feet long, or if they would happen to be above grade when finished.
Some people don't feel this way, and some inspectors would let you tie to a 6 inch piece as long as it is tied "with the usual ties" to at least 20 feet somehow. I can kind of see where that comes from, but if presented with what we see in the picture why not tie to a horizontal bar instead of a vertical bar? It takes pretty much the same effort and removes any doubt of whether or not the vertical piece is acceptable.
The code posted in post 7 clearly allows for multiple rods tied together to form a 20 foot rod, but I myself do not feel that the cross tied rods meet the intent of "usual steel tie wires" or "other effective means" if we think logically we know these very minimal connection points will not last very long, but then again how long will uncoated rebar last in concrete in damp ground???
250.52(A)(3) Concrete-Encased Electrode. A concrete-encased
electrode shall consist of at least 6.0 m (20 ft) of either
(1) or (2):
(1) One or more bare or zinc galvanized or other electri-
cally conductive coated steel reinforcing bars or rods of
not less than 13 mm (1⁄2 in.) in diameter, installed in
one continuous 6.0 m (20 ft) length, or if in multiple
pieces connected together by the usual steel tie wires,
exothermic welding, welding, or other effective means
to create a 6.0 m (20 ft) or greater length; or