allenwayne said:The nec says that there has to be gfci protection,afci protection,spacing etc.It does not state that an inspector has to ensure that it works .
If you don't check if it works, how do you know that it's GFCI or AFCI protected ?
allenwayne said:As long as the proper stickers say gfci protected the panel says bedrooms are afci protected the spacing is correct and all looks compliant then unless a jurisdiction has an addendum on record that these items will be checked to ensure they operate as intended then this is a redundant conversation.
"proper stickers say gfci"
Not only are stickers not required but all they are is a promise. "I promise that I installed it right !"
Like mpd said:
mpd said:as far as the final inspection with no power, doing a final inspection without power is a joke, why not just have the contractor send pictures and pass them from the office, I would NEVER sign my name to a final with no power.
I would like someone to answer that question. If there's no power for the final, why not just have the contractor send pictures and pass them from the office ?
allenwayne said:We have hashed and rehashed the A/C breaker sizing over and over but if the name plate says min 20 amps for min. cir. ampacity and had a 60 listed as the max breaker size we don`t have to size the conductors for the max breaker size.If you can show mw where in the NEC it says that the install will work I will say you are correct.
I?m not sure who this thought is directed to. Was someone talking about AC circuit sizing ?
allenwayne said:The fact is it says what is required as a min. and as long as that is met and/or unless there is a local addendum to supercide it then power is not a requirement for a final.Yes that does open a whole can of worms but once the AHJ signs it off it is visually code compliant and thats the NEC requirement.
?it is visually code compliant and thats the NEC requirement?
Your position is that the NEC is a visual inspection code ?
I couldn?t disagree more strongly !
allenwayne said:Is it right not in my opinion but how many inspections could you do in a day checking every light gfci afci etc.
Our inspectors have usually 35 to 60 inspections/ day 5 to 6 days a week thats per inspector ,one county here has about 10 inspectors so thats 350 to 600 inspections / day and if they roll an inspection its a domino effect.
NOW we?re getting to the real heart of your position. It has nothing to do with how proper inspections should be done. This is all about saving the building department the money of hiring the needed amount of inspectors to do the job correctly. If your inspectors have 35 to 60 inspections a day, you don?t have enough inspectors.
60 inspections over 8 hours averages starting a different inspection every 8 minutes. And travel time is included in that 8 minutes.
Our quickest simplest inspection is a trench inspection and I probably couldn?t do 60 of them in a day even if I drove a dragster from site to site.
If all that matters is production and not quality of the job done, why not just have the contractor send pictures and pass them from the office ?
If the AHJ doesn?t want to hire the necessary manpower, why bother calling it a building department ? Just call it a consulting department.