Preach it!4 breaker outdoor panel and be done with it. What HVAC tech runs a vacuum pump when the mini-split is running?
The usual way, the 240.4(G) allowance for motor circuits covers a feeder supplying a motor and other loads, something Article 430 addresses directly. So assuming the AC cable is not run through insulation (2020 320.80(A)), you can use #10 Cu at its 75C ampacity of 35A.I don't see how you could use a 35 amp OCPD on #10 conductors.
I actually don't want to use a subpanel all I plan to do is put a splice box and tap the number 10 to two separate disconnects
Sent from my SM-S906U using Tapatalk
Still doesn't get around the amperage issue, but you theoretical could so long as it is not on a removable panel. But not sure it would satisfy the intent of having the Maintenance receptacle near the AC, as it would still need to be present for installation or removal/replacement of unit. Also the receptacle not be connected to the load side of the equipment disconnect (210.63)I know nothing, but wouldn't it be cool if you could mount a WP receptacle outlet right on the AC unit itself? Splice it on the inside of the unit.
That would violate 210.63: The receptacle outlet shall not be connected to the load side of the equipment disconnecting means.Splice it on the inside of the unit.
210.23(A)(2) Utilization Equipment Fastened in Place.
The total rating of utilization equipment fastened in place, other than luminaires, shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.
I don't see how the exception would apply to a Minisplit unit.Also if this us a 1 or 2 family dwelling unit the 210.63 exception would apply and you don't even need one.
So what size breakers did you use? My reading (see above) is you could use a 40A for the 10/3 75C feeder, and a 25A for the minisplit, and a 15A for the receptacle.Any way we went ahead just put a small panel in as some suggested and turned the AC circuit into a feeder.
The service/Maintenance receptacle, the mini split has an AC Compressor unit just like any other AC, the service receptacle that would be near the compressor would not necessarily be required in a 1 or 2 family dwelling.I don't see how the exception would apply to a Minisplit unit.
I'm not sure I follow you. 210.63 requires a service receptacle near the compressor at 1 or 2 family dwellings just as it does at non-dwellings.The service/Maintenance receptacle, the mini split has an AC Compressor unit just like any other AC, the service receptacle that would be near the compressor would not necessarily be required in a 1 or 2 family dwelling.
2017 210.63 exception: A receptacle outlet shall not be required at one- and two- family dwelling for the service of evaporative coolers.I'm not sure I follow you. 210.63 requires a service receptacle near the compressor at 1 or 2 family dwellings just as it does at non-dwellings.
Is that this beastie?Could have used something similar to this AC disconnect.
I said similar, I seem to recall some having internal OCP for the receptacle. I haven't used one in ten + years.Is that this beastie?
![]()
GE 60 Amp 240-Volt Non-Fuse AC Disconnect with GFCI Receptacle TFN60RGFRCP - The Home Depot
Find the 60 amp 240-Volt 14,400-Watt Non-Fuse Metallic AC Disconnect with GFCI Receptacle TFN60RGFRCP, AC stop the flow of power to your air conditioner to ensure secure working conditions during maintenancewww.homedepot.com
From the documentation it isn't clear if the GFCI is tapped from the HVAC circuit, or if you need a separate circuit to feed the receptacle. I strongly suspect the latter.
-Jon