Receptacle spacing in a kitchen

Status
Not open for further replies.

A/A Fuel GTX

Senior Member
Location
WI & AZ
Occupation
Electrician
Can receptacles serving kitchen countertops and islands be used to satisfy the wall space requirements for receptacles?

Example:
An island has a receptacle that would be within 6' of an adjacent wall in a kitchen. The wall section is about 7' long. Would the island receptacle eliminate the need for a receptacle on the wall?
 
Can receptacles serving kitchen countertops and islands be used to satisfy the wall space requirements for receptacles?

Example:
An island has a receptacle that would be within 6' of an adjacent wall in a kitchen. The wall section is about 7' long. Would the island receptacle eliminate the need for a receptacle on the wall?

I would say no. But it could be feed from one of the sabc as long as it was in the kitchen.
 
Actually I've never thought about this. I've always installed the wall receptacles separate. But now that the question is raised--why not include it? As long as the receptacles are below 5 1/2 feet, I see no reason why it couldn't be installed, and included in the spacing requirement.
 
A kitchen cir can be no more than 3 recep right?
You only needed 2 for your countertop, why not be able to use the 3rd to satisfy a wall space? :)
 
I just looked through that and could not find a restriction on the number of receps on a "small-appliance" cir. .....

That's because it isn't there. :cool:

I do recall some GFI's having instructions about the number of 'downstream' receps they allow, but that's a listing issue and not an NEC. local codes, of course, may dictate otherwise.

Rephrase: In my area, I must have 2 (We call them "kitchen circuits", they are for the countertops) small-appliance branch circuits and I can not have more that 3 receps on that circuit.

Im on the 2002 NEC

Your SABCs must stay on the countertops, despite 210.52(B)(1)'s wording?
 
What I am getting at is the wall that is 7' long needs it's own receptacle on it because the island is not attached to it. Thus "island". so the wall spacing requirements of 210.52 (A) apply to the wall.
 
What I am getting at is the wall that is 7' long needs it's own receptacle on it because the island is not attached to it. Thus "island". so the wall spacing requirements of 210.52 (A) apply to the wall.
I agree, if we base it on the OP's example! :)
 
That's because it isn't there. :cool:

I do recall some GFI's having instructions about the number of 'downstream' receps they allow, but that's a listing issue and not an NEC. local codes, of course, may dictate otherwise.



Your SABCs must stay on the countertops, despite 210.52(B)(1)'s wording?

?????????? Splain your selp Lucy.
 
Last edited by a moderator:
That's because it isn't there. :cool:

I do recall some GFI's having instructions about the number of 'downstream' receps they allow, but that's a listing issue and not an NEC. local codes, of course, may dictate otherwise.



Your SABCs must stay on the countertops, despite 210.52(B)(1)'s wording?

Sorry. I was refering to the countertops because that is for reference. I should have inclluded "and for like the fridge" :p
 