The following wasn't directed to me but I want to put in my 2 cents anyway.
I checked with a fellow inspector and have returned armed with his thoughts.
bikeindy said:
Using your reasoning, if we are connecting any item in 400.7(A) we could use flexible cords for the following;
- (1) As a substitute for the fixed wiring of a structure
- (2) To run through holes in walls, structural ceilings, suspended ceilings, dropped ceilings, or floors
- (3) To run run through doorways, windows, or similar openings
- (4) Attached to building surfaces
- (5) Concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
- (6) Where installed in raceways, except as otherwise permitted in this Code
- (7) Where subject to physical damage
because 400.7(A) includes them, is this correct?
"if we are connecting any item in 400.7(A) we could use flexible cords for the following;"
"because 400.7(A) includes them, is this correct?"
I would answer,
Yes, if manufacturers instructions
specifically permit it.
And 400.8(4)x says you don't even need a manufacturers OK to attach a cord from a busway to the building surface.
bikeindy said:
If it is correct, why would the ink be wasted for 400.8?
Part of the ink in 400.8 says, "Unless specifically permitted in 400.7"
So the ink in 400.8 applies only to installations that
don't fall under 400.7
Those first 5 words of 400.8 state that 400.7 "trumps" 400.8
if it is
specifically listed in manufacturers instructions as being permitted.
Another example is 400.8(6) & (7) which is modified by 400.14. And you can use what's allowed in 400.14 without the manufacturers specifically saying that it's OK. You can follow that section unless the manufacturer has specific wording that
excludes installing as described in 400.14.
400.8 is the other way around. You can not use a cord in an installation described in 400.8 unless the manufacturer has specific wording that
includes installing as described in 400.7
The 400.8 restrictions are not absolute.
bikeindy said:
I don't see how you reason that out those items are not listed in 400.7
I think there is something missing in this section of the post. Maybe there was supposed to be a quote that didn't make it into the final post.
David