So I can check line-line when needed.
Apparently, we're checking two different things. I'm using the bulb to locate a short circuit (to ground) somewhere in the circuit. Line-to-line shorts are much easier to locate.
I was not clear.Apparently, we're checking two different things. I'm using the bulb to locate a short circuit (to ground) somewhere in the circuit. Line-to-line shorts are much easier to locate.
I was not clear.
I use the same gear when I'm checking a panel for blown fuses, water heaters, etc. It is easier for a quick diagnosis than a meter and travels light.
The ballast wire works great on some of the old fuse blocks because it will fit right into the little holes on the front and you can make a quick check without even removing the panel cover.
Take to the door on a lot of resi/small com trouble calls: toolbelt, screwgun, flashlight, testlight.Ok, we're on opposite sides of the planet. I install a temp sockets with lamps at the panel to locate shorts to ground. I install one between the breaker/fuse and the branch circuit ungrounded, and the other between the fuse/breaker and ground.
If both lamps are the same brightness, there's a short somewhere. When the bulb attached to the circuit's hot dims or goes out, the short is no longer there.
I can't imagine using a lamp just to check voltage...... there's too many meters out there that will do the same thing, and I don't have to worry about breaking them.
I understand that. But I don't like to keep tripping a breaker or spending 25 bucks on fuses trying to locate a short to ground. That's why I use the lamps.
Doesn't the second bulb just burn at full brilliance, and merely act as a power indicator?I use two bulbs, one installed in the 'trouble' circuit, and the other between the breaker or fuse and ground. If the two are the same brightness, there's still a short. If the 'problem' circuit bulb dims or goes out, then the problem is solved.
So, you're talking about the fuse-clip access holes on the pull-outs. My K-60's probes fit those holes.The ballast wire works great on some of the old fuse blocks because it will fit right into the little holes on the front and you can make a quick check without even removing the panel cover.
In other words, in series with the circuit, as a combination current-limiter and indicator. Black wire to fuse/breaker, white to circuit.I install a temp sockets with lamps at the panel to locate shorts to ground.
I guess having a brightness-comparison helps for circuits with loads still plugged in/turned on, but I've never needed one.I install one between the breaker/fuse and the branch circuit ungrounded, and the other between the fuse/breaker and ground.
When we find a short and make the contact intermittent or clear it, there's no mistaking the variations in bulb brightness.
Some are big holes, some are real small. I can carry the test light around by the leads, and don't have to find a place for a meter, and it is super light (weight, not lumens).So, you're talking about the fuse-clip access holes on the pull-outs. My K-60's probes fit those holes.
Get Rid Of The Fuses.
I'm trying to figure out exactly how you utilize this troubleshooting method.
1) If you have a short circuit (to ground) wouldnt the breaker trip whenever moved to the 'on' position? I understand how you would use a lamp connected from the breaker to ground as a brightness reference. Why would a lamp (temporarily) wired in series with the branch circuit off the same breaker dim when the short is removed (assuming there is no other load on the circuit)?........
Thanks for the explaination. I should have been able to figure that out by myself.
Just an update, I forgot about this thread. Got to the house and checked fuse panel. Checked voltage from service..good. Checked termination of conductors at problem branch circuit..good.(only one wire landed at fuse terminal !!) Went to outlet receptacles of branch circuit. Checked voltage at each receptacle.. good. Looked for problem appliances on circuit in bedroom..only an alarm clock??? Master bedroom is an addition to house. Decided to eyeball wiring in attic. Traced romex down..looked ok?? Followed homerun down back to panel..looked good! Noticed a junction box in home run?? Feed a small attic exhaust fan, motor was locked down!! When homeowner said she was blowing a fuse when nothing was on circuit, she did not realize the fan was on this circuit. Thermostat would call for fan to run and fuse would blow. Thanks for all of your comments!!:smile: