This may or may not be relevant, I had a case of arcing in a home between gas and water lines...
looked and there was no jumper around water meter..installed one. Arcing went away, obviously the current in the water lines was seeking a return path, which led me to the panel.
Visual inspection didnt reveal any severe problems until we plugged in a sawzall...then Saw a spark behind the main neutral lug. Rotted away from moisture,
Everything was returning basically on the water electrode bond...replaced panel.
You never know what’s truly bonded or connected in older homes, what has a good grounded current carrying conductor.