Yeah thats what he failed me on no red identification, I thought for sure he'd want a AFCI, I had intended to wirenut it onto a AFCI bedroom lighting circuit in the panel.
If the following conditions were met it could be a NPLFA circuit;
Had to be
- on a circuit with no loads other than somke / heat or combo CO detectors ,
- battery backed,
- inter connected and have a hush button (thus forming a system)
to qualify as a NPLFA circuit then 760.41(b) and 760.3 applies so I guess they had a meeting about it, I just checked the state code and there is no amendments so its an interpretation of a non-NEC defined term a 'fire alarm system'. In the definition in NFPA 72 of 'fire alarm system' pretty general in scope;
They look at the risks pros/cons I guess they think its more important smoke / heat / CO alarms have reliable 120V power than any benefits AFCI protecting such a circuit would offer.